[<prev] [next>] [<thread-prev] [thread-next>] [day] [month] [year] [list]
Message-ID: <5242771E.4080202@freescale.com>
Date: Wed, 25 Sep 2013 13:39:42 +0800
From: Hongbo Zhang <hongbo.zhang@...escale.com>
To: Eduardo Valentin <eduardo.valentin@...com>
CC: Mark Rutland <mark.rutland@....com>,
"swarren@...dotorg.org" <swarren@...dotorg.org>,
Pawel Moll <Pawel.Moll@....com>,
"ian.campbell@...rix.com" <ian.campbell@...rix.com>,
"rob.herring@...xeda.com" <rob.herring@...xeda.com>,
"linux@...ck-us.net" <linux@...ck-us.net>,
"rui.zhang@...el.com" <rui.zhang@...el.com>,
"wni@...dia.com" <wni@...dia.com>,
"joe@...ches.com" <joe@...ches.com>,
"grant.likely@...aro.org" <grant.likely@...aro.org>,
"durgadoss.r@...el.com" <durgadoss.r@...el.com>,
"lm-sensors@...sensors.org" <lm-sensors@...sensors.org>,
"linux-kernel@...r.kernel.org" <linux-kernel@...r.kernel.org>,
"linux-pm@...r.kernel.org" <linux-pm@...r.kernel.org>
Subject: Re: [PATCHv6 02/16] drivers: thermal: introduce device tree parser
On 09/24/2013 11:50 PM, Eduardo Valentin wrote:
> Zhang,
>
> I appreciate your interest. I am replying a couple of your comments.
> Please also check my answers to Mark's queries on other email thread.
When I replied to Mark yesterday, I missed your mail replying him already.
I should check that mail and reply it for further concerns.
> On 24-09-2013 04:11, Hongbo Zhang wrote:
>> On 09/23/2013 06:40 PM, Mark Rutland wrote:
>>> Hi Eduardo,
>>>
>>> Apologies for having taken so long to get back you on this.
>>>
>>> I have several comments on the binding and the way it's parsed.
>>>
>>> On Wed, Sep 18, 2013 at 10:35:36PM +0100, Eduardo Valentin wrote:
>>>> This patch introduces a device tree bindings for
>>>> describing the hardware thermal behavior and limits.
>>>> Also a parser to read and interpret the data and feed
>>>> it in the thermal framework is presented.
>>>>
>>>> This patch introduces a thermal data parser for device
>>>> tree. The parsed data is used to build thermal zones
>>>> and thermal binding parameters. The output data
>>>> can then be used to deploy thermal policies.
>>>>
>>>> This patch adds also documentation regarding this
>>>> API and how to define tree nodes to use
>>>> this infrastructure.
>>>>
>>>> Note that, in order to be able to have control
>>>> on the sensor registration on the DT thermal zone,
>>>> it was required to allow changing the thermal zone
>>>> .get_temp callback. For this reason, this patch
>>>> also removes the 'const' modifier from the .ops
>>>> field of thermal zone devices.
>>>>
>>>> Cc: Zhang Rui <rui.zhang@...el.com>
>>>> Cc: linux-pm@...r.kernel.org
>>>> Cc: linux-kernel@...r.kernel.org
>>>> Signed-off-by: Eduardo Valentin <eduardo.valentin@...com>
>>>> ---
>>>> .../devicetree/bindings/thermal/thermal.txt | 498 +++++++++++++
>>>> drivers/thermal/Kconfig | 13 +
>>>> drivers/thermal/Makefile | 1 +
>>>> drivers/thermal/of-thermal.c | 775
>>>> +++++++++++++++++++++
>>>> drivers/thermal/thermal_core.c | 9 +-
>>>> drivers/thermal/thermal_core.h | 9 +
>>>> include/dt-bindings/thermal/thermal.h | 27 +
>>>> include/linux/thermal.h | 28 +-
>>>> 8 files changed, 1357 insertions(+), 3 deletions(-)
>>>> create mode 100644
>>>> Documentation/devicetree/bindings/thermal/thermal.txt
>>>> create mode 100644 drivers/thermal/of-thermal.c
>>>> create mode 100644 include/dt-bindings/thermal/thermal.h
>>>>
>>>> ---
>>>>
>>>> Hello all,
>>>>
>>>> Thanks Joe Perches for the effort of reviewing this code, I really
>>>> appreciate it.
>>>>
>>>> Here is a version with a refactored init function without leaks in
>>>> the failure
>>>> patch. I also added a couple of comments to better understand the
>>>> intention of
>>>> that function. Besides, when there are no memory available, the function
>>>> rolls back what ever thermal zones have been added.
>>>>
>>>> Thanks,
>>>>
>>>> Eduardo
>>>>
>>>> diff --git a/Documentation/devicetree/bindings/thermal/thermal.txt
>>>> b/Documentation/devicetree/bindings/thermal/thermal.txt
>>>> new file mode 100644
>>>> index 0000000..6664533
>>>> --- /dev/null
>>>> +++ b/Documentation/devicetree/bindings/thermal/thermal.txt
>>>> @@ -0,0 +1,498 @@
>>>> +* Thermal Framework Device Tree descriptor
>>>> +
>>>> +Generic binding to provide a way of defining hardware thermal
>>>> +structure using device tree. A thermal structure includes thermal
>>>> +zones and their components, such as trip points, polling intervals,
>>>> +sensors and cooling devices binding descriptors.
>>>> +
>>>> +The target of device tree thermal descriptors is to describe only
>>>> +the hardware thermal aspects, not how the system must control or which
>>>> +algorithm or policy must be taken in place.
>>>> +
>>>> +There are five types of nodes involved to describe thermal bindings:
>>>> +- sensors: used to describe the device source of temperature sensing;
>>>> +- cooling devices: used to describe devices source of power
>>>> dissipation control;
>>>> +- trip points: used to describe points in temperature domain defined to
>>>> +make the system aware of hardware limits;
>>>> +- cooling attachments: used to describe links between trip points and
>>>> +cooling devices;
>>> I think "attachments" sounds a bit odd, though I don't have a better
>>> naming suggestion.
>> "map" or "mapping" is better?
> Well, yeah, that could work.
:)
>>>> +- thermal zones: used to describe thermal data within the hardware;
>>>> +
>>>> +It follows a description of each type of these device tree nodes.
>>>> +
>>>> +* Sensor devices
>>>> +
>>>> +Sensor devices are nodes providing temperature sensing capabilities
>>>> on thermal
>>>> +zones. Typical devices are I2C ADC converters and bandgaps. Theses
>>>> are nodes
>>>> +providing temperature data to thermal zones. Temperature sensor
>>>> devices may
>>>> +control one or more internal sensors.
>>>> +
>>>> +Required property:
>>>> +- #sensor-cells: Used to provide sensor device specific
>>>> information
>>>> + while referring to it. Must be at least 1, in
>>>> order
>>>> + to identify uniquely the sensor instances within
>>>> + the IC. See thermal zone binding for more
>>>> details
>>>> + on how consumers refer to sensor devices.
>>> I don't see why this needs to be at least one cell -- if an IC only has
>>> one temperature sensor it should be fine for this to be zero and have no
>>> ambiguity.
>>>
>>> It may make sense to call these thermal sensor devices, there are plenty
>>> of other sensors we might want to describe in the dt for other purposes,
>>> and we can impose some consistency if we remove the ambiguity.
>>>
>>>> +
>>>> +* Cooling device nodes
>>>> +
>>>> +Cooling devices are nodes providing control on power dissipation. There
>>>> +are essentially two ways to provide control on power dissipation. First
>>>> +is by means of regulating device performance, which is known as passive
>>>> +cooling. Second is by means of activating devices in order to remove
>>>> +the dissipated heat, which is known as active cooling, e.g. regulating
>>>> +fan speeds. In both cases, cooling devices shall have a way to
>>>> determine
>>>> +the level of cooling.
>>>> +
>>>> +Required property:
>>>> +- cooling-min-level: A unsigned integer indicating the smallest
>>>> + cooling level accepted. Typically 0.
>>>> +- cooling-max-level: An unsigned integer indicating the largest
>>>> + cooling level accepted.
>>> I'm not sure what a "cooling level" means. It seems a bit abstract. Is
>>> this binding specific?
>> It means cooling ability of a cooling device, such as speed of a fan.
>> But it is better to use cooling-min/max-state I think, because the
>> thermal management code is using "cooling state", concepts in dt and c
>> should be identical.
> I think the idea is just to be clear. Just because the thermal
> management implementation uses a terminology, it does not necessarily
> mean it is best fit for describing in device tree bindings. But I dont
> really have strong opinion on level or state at this point.
>
>>> How does this relate to cooling-cells? These seem to be a fixed size.
>> I also think cooling-cells is redundant.
> Cooling cells is not redundant, please check my explanation on the other
> thread. It is required to determine which level/states are used while
> binding.
>
OK
>>>> +- #cooling-cells: Used to provide cooling device specific
>>>> information
>>>> + while referring to it. Must be at least 2, in
>>>> order
>>>> + to specify minimum and maximum cooling level
>>>> used
>>>> + in the reference. See Cooling device
>>>> attachments section
>>>> + below for more details on how consumers refer to
>>>> + cooling devices.
>>> Are these cooling cells always expected to cover min and max, and are
>>> min and max always expected to take the same number of cells? The above
>>> cooling-*-level properties imply they each take up one cell.
>>>
>>> Does #cooling-cells = <3> make sense?. If this covers additional
>>> information (e.g. which fan on a multi-fan controller), how does the OS
>>> determine which cells are min and max, and how do these relate to
>>> cooling-level-min and cooling-level-max?
>>>
>>>> +
>>>> +* Trip points
>>>> +
>>>> +The trip node is a node to describe a point in the temperature domain
>>>> +in which the system takes an action. This node describes just the
>>>> point,
>>>> +not the action.
>>> I'm still not sure on this, as it sounds like embedding policy into the
>>> DT, rather than a description of the hardware. I realise we need to
>>> prevent devices burning out, so describing the max acceptable
>>> temperature and possibly a preferred range makes sense, but do we need
>>> this level of flexibility? Maybe we do.
>>>
>> Putting platform data into dt is acceptable, right?
>> In a narrow sense, trip points are platform data, but in a broad sense,
>> both trip point itself and its corresponding cooling device are all
>> platform data.
>>
> I think Mark needs to elaborate a bit more to clarify why he sees this
> as embedding policy into DT. And I believe it is fine to pass platform
> data, as long as it represents hardware and it is not representing policy.
>
>>>> +
>>>> +Required properties:
>>>> +- temperature: the trip temperature level, in milliCelsius.
>>> Preferably, s/milliCelsius/millicelsius/ over the document.
>>>
>>> Given that we have signed values elsewhere, is this signed or unsigned?
>>>
>>>> +- hysteresis: a (low) hysteresis value on 'temperature'.
>>>> This is a
>>>> + relative value, in milliCelsius.
>>>> +- type: the trip type. Here is the type mapping:
>>>> + THERMAL_TRIP_ACTIVE 0: A trip point to enable active
>>>> cooling
>>>> + THERMAL_TRIP_PASSIVE 1: A trip point to enable
>>>> passive cooling
>>>> + THERMAL_TRIP_HOT 2: A trip point to notify emergency
>>>> + THERMAL_TRIP_CRITICAL 3: Hardware not reliable.
>>>> +
>>>> +Refer to include/dt-bindings/thermal/thermal.h for definition of
>>>> these consts.
>>> Why not use a string for this? We do so for other type parameters in
>>> other bindings (see dr_mode in
>>> Documentation/devicetree/bindings/usb/generic.txt, phy-mode for ethernet
>>> PHYs, etc).
>>>
>>>> +
>>>> +* Cooling device attachments
>>>> +
>>>> +The cooling device attachments node is a node to describe how
>>>> cooling devices
>>>> +get assigned to trip points of the zone. The cooling devices are
>>>> expected
>>>> +to be loaded in the target system.
>>>> +
>>>> +Required properties:
>>>> +- cooling-device: A phandle of a cooling device with its
>>>> parameters,
>>>> + referring to which cooling device is used in
>>>> this
>>>> + binding. The required parameters are: the
>>>> minimum
>>>> + cooling level and the maximum cooling level used
>>>> + in this attach.
>>> Might this be a list in general? The code doesn't have to support that
>>> yet.
>>>
>>> It would be nice to have a name for the cells after a phandle which
>>> describe the cooling device's configuration. You've called them
>>> parameters here, but it probably makes sense to call them a
>>> cooling-specifier (following clock-specifier and interrupt-specifier).
>>>
>>>> +- trip: A phandle of a trip point node within
>>>> the same thermal
>>>> + zone.
>>>> +
>>>> +Optional property:
>>>> +- contribution: The cooling contribution to the
>>>> thermal zone of the
>>>> + referred cooling device at the referred trip
>>>> point.
>>>> + The contribution is a value from 0 to 100.
>>>> The sum
>>>> + of all cooling contributions within a thermal
>>>> zone
>>>> + must never exceed 100.
>>> This is a bit arbitrary. Couldn't we sum all contributions to find the
>>> total automatically, so this could be a simpler ratio?
>>>
>>>> +
>>>> +Note: Using the THERMAL_NO_LIMIT (-1L) constant in the
>>>> cooling-device phandle
>>>> +limit parameters means:
>>>> +(i) - minimum level allowed for minimum cooling level used in the
>>>> reference.
>>>> +(ii) - maximum level allowed for maximum cooling level used in the
>>>> reference.
>>>> +Refer to include/dt-bindings/thermal/thermal.h for definition of
>>>> this constant.
>>>> +
>>>> +* Thermal zones
>>>> +
>>>> +The thermal-zone node is the node containing all the required info
>>>> +for describing a thermal zone, including its cdev bindings. The
>>>> thermal_zone
>>>> +node must contain, apart from its own properties, one node containing
>>>> +trip nodes and one node containing all the zone cooling attachments.
>>> s/cdev/cooling device/ ?
>>>
>>>> +
>>>> +Required properties:
>>>> +- passive-delay: The maximum number of milliseconds to wait
>>>> between polls
>>>> + when performing passive cooling.
>>>> +- polling-delay: The maximum number of milliseconds to wait
>>>> between polls
>>>> + when checking this thermal zone.
>>> How about polling-delay-passive, polling-delay-active? I'm still not
>>>
>>>> +- sensors: A list of sensor phandles and their
>>>> parameters. The
>>>> + required parameter is the sensor id, in order to
>>>> + identify internal sensors when the sensor IC
>>>> features
>>>> + several sensing units.
>>> As mentioned above, I'm not sure you even need that one cell.
>>>
>>> - sensors: A list of sensor phandle +
>>> thermal-sensor-specifier
>>> cells describing the sensors monitoring the
>>> thermal
>>> zone.
>>>
>>>> +- trips: A sub-node containing several trip point
>>>> nodes required
>>>> + to describe the thermal zone.
>>>> +- cooling-attachments A sub-node containing several cooling device
>>>> attaches
>>>> + nodes, used to describe the relation between
>>>> trips
>>>> + and cooling devices.
>>>> +
>>>> +Optional property:
>>>> +- coefficients: An array of integers (one signed
>>>> cell) containing
>>>> + coefficients to compose a linear relation
>>>> between
>>>> + the sensors described in the sensors property.
>>>> + Coefficients defaults to 1, in case this
>>>> property
>>>> + is not specified. A simple linear polynomial
>>>> is used:
>>>> + Z = c0 * x0 + c1 + x1 + ... + c(n-1) * x(n-1)
>>>> + cn.
>>>> +
>>>> + The coefficients are ordered and they match
>>>> with sensors
>>>> + by means of sensor ID. Additional
>>>> coefficients are
>>>> + interpreted as constant offsets.
>>> What is the end result of this? Presumably this is meant to result in an
>>> estimate of the average temperature of the thermal zone, rather than an
>>> arbitrary value? This should be mentioned.
>>>
>>> This doesn't seem to be used the in the code below...
>>>
>>>> +
>>>> +Note: The delay properties are bound to the maximum dT/dt (temperature
>>>> +derivative over time) in two situations for a thermal zone:
>>>> +(i) - when active cooling is activated (passive-delay); and
>>>> +(ii) - when the zone just needs to be monitored (polling-delay).
>>>> +The maximum dT/dt is highly bound to hardware power consumption and
>>>> dissipation
>>>> +capability.
>>> I'm not sure what you mean by this, could you elaborate?
>>>
>>> I guess you mean that the delays should be chosen to account for said
>>> max dT/dt, such that a device can't unexpectedly cross several trip
>>> boundaries between polls?
>>>
>>>> +
>>>> +* Examples
>>>> +
>>>> +Below are several examples on how to use thermal data descriptors
>>>> +using device tree bindings:
>>>> +
>>>> +(a) - CPU thermal zone
>>>> +
>>>> +The CPU thermal zone example below describes how to setup one
>>>> thermal zone
>>>> +using one single sensor as temperature source and many cooling
>>>> devices and
>>>> +power dissipation control sources.
>>>> +
>>>> +#include <dt-bindings/thermal/thermal.h>
>>>> +
>>>> +cpus {
>>>> + cpu0: cpu@0 {
>>>> + ...
>>>> + cooling-min-level = <0>;
>>>> + cooling-max-level = <3>;
>>>> + #cooling-cells = <2>; /* min followed by max */
>>>> + };
>>> What do those min and max mean in this context? What do the values in
>>> the range [0,3] correspond to?
>>>
>>> I'm not sure it makes sense to describe passive cooling in this way --
>>> the precise way an OS does less work on a device is fundamentally tied
>>> to the design of the OS (it might be able to rate-limit requests, it
>>> might be able to clock the device down, it might only be able to turn
>>> the device off).
>>>
>>> I'm not sure there is anything we can describe for passive cooling
>>> (beyond the thermal limits the OS should attempt to stick to).
>>>
>>>> + ...
>>>> +};
>>>> +
>>>> +&i2c1 {
>>>> + ...
>>>> + fan0: fan@...8 {
>>>> + ...
>>>> + cooling-min-level = <0>;
>>>> + cooling-max-level = <9>;
>>>> + #cooling-cells = <2>; /* min followed by max */
>>>> + };
>>> What do min and max mean here for the fan?
>>>
>> It means the speed level of a fan. Even if a fan can run at a continuous
>> speed range, but when it is controlled under thermal management
>> framework, it can only run at discrete speeds.
>
> Please, an important point here, this is not about thermal framework
> requirement. But how we describe hardware. As you mentioned, even if
> there are fan devices out there that uses continuous speed range, there
> other devices, even fan devices or cpu frequency steps for instance,
> that are discrete. Again, *this is not a thermal framework requirement*.
>
>>>> +};
>>>> +
>>>> +bandgap0: bandgap@...000ED00 {
>>>> + ...
>>>> + #sensor-cells = <1>;
>>>> +};
>>>> +
>>>> +cpu-thermal: cpu-thermal {
>>> How do the thermal zones get probed?
>>>
>>>> + passive-delay = <250>; /* milliseconds */
>>>> + polling-delay = <1000>; /* milliseconds */
>>>> +
>>>> + /* sensor ID */
>>>> + sensors = <&bandgap0 0>;
>>>> +
>>>> + trips {
>>>> + cpu-alert0: cpu-alert {
>>>> + temperature = <90000>; /* milliCelsius */
>>>> + hysteresis = <2000>; /* milliCelsius */
>>>> + type = <THERMAL_TRIP_ACTIVE>;
>>>> + };
>>>> + cpu-alert1: cpu-alert {
>>>> + temperature = <100000>; /* milliCelsius */
>>>> + hysteresis = <2000>; /* milliCelsius */
>>>> + type = <THERMAL_TRIP_PASSIVE>;
>>>> + };
>>>> + cpu-crit: cpu-crit {
>>>> + temperature = <125000>; /* milliCelsius */
>>>> + hysteresis = <2000>; /* milliCelsius */
>>>> + type = <THERMAL_TRIP_CRITICAL>;
>>>> + };
>>>> + };
>>>> +
>>>> + cooling-attachments {
>>>> + attach0 {
>>>> + trip = <&cpu-alert0>;
>>>> + cooling-device = <&fan0 THERMAL_NO_LIMITS 4>;
>>>> + };
>>>> + attach1 {
>>>> + trip = <&cpu-alert1>;
>>>> + cooling-device = <&fan0 5 THERMAL_NO_LIMITS>;
>>>> + };
>>>> + attach2 {
>>>> + trip = <&cpu-alert1>;
>>>> + cooling-device =
>>>> + <&cpu0 THERMAL_NO_LIMITS
>>>> THERMAL_NO_LIMITS>;
>>>> + };
>>>> + };
>>> Was there a good reason for splitting trips and attachment?
>> This is for adding/removing cooling device dynamically.
> Well not really. I don't think this would prevent us of representing it
> inside the trip point. It is, as I replied to Mark, because I wanted to
> keep the flexibility to allow describing better properties related to
> the cooling device while associated to a trip point alone, e.g.
> 'contribution'.
Understand your purpose and explanation.
But this can also really help to add/remove cooling device freely, there
were already drivers with separated files of thermal zone and cooling
device.
>>>> +};
>>>> +
>>>> +In the example above, the ADC sensor at address 0x0000ED00 is used
>>>> to monitor
>>>> +the zone 'cpu-thermal' using its the sensor 0. The fan0, a fan
>>>> device controlled
>>>> +via I2C bus 1, at adress 0x48, is used to remove the heat out of the
>>>> thermal
>>>> +zone 'cpu-thermal' using its cooling levels from its minimum to 4,
>>>> when it
>>>> +reaches trip point 'cpu-alert0' at 90C, as an example of active
>>>> cooling. The
>>>> +same cooling device is used at 'cpu-alert1', but from 5 to its
>>>> maximum level.
>>>> +The cpu@0 device is also linked to the same thermal zone,
>>>> 'cpu-thermal', as a
>>>> +passive cooling device, using all its cooling levels at trip point
>>>> 'cpu-alert1',
>>>> +which is a trip point at 100C.
>>>> +
>>
>>
>>
>>
>
--