Subject: Re: [PATCH 11/15] thermal: thermal: Add support for hardware-tracked
trip points
On Mon, May 18, 2015 at 02:09:44PM +0200, Sascha Hauer wrote:
> On Mon, May 18, 2015 at 12:06:50PM +0300, Mikko Perttunen wrote:
> > One interesting thing I noticed was that at least the bang-bang
> > governor only acts if the temperature is properly smaller than (trip
> > temp - hysteresis). So perhaps we should specify the non-tripping
> > range as [low, high)? Or we could change bang-bang.
>
> I wonder how we can protect against such off-by-one errors anyway.
> Generally a hardware might operate on raw values rather than directly
> in temperature values in °C. This means a driver for this must have
> celsius_to_raw and raw_to_celsius conversion functions. Now it can
> happen that due to rounding errors celsius_to_raw(Tcrit) returns a raw
> value that when converted back to celsius is different from the
> original value in °C. This would mean the hardware triggers an interrupt
> for a trip point and the thermal core does not react because get_temp
> actually returns a different temperature than previously programmed as
> interrupt trigger. This way we would lose hot (or cold) events.
This also highlights another fact: there's a race between interrupt
generation and temperature reading (->get_temp()). I would expect any
hardware interrupt thermal sensor would also have a latched temperature
reading to correspond with it, and there would be no guarantee that this
latched temperature will match the polled reading seen once you reach
thermal_zone_device_update(). So a hardware driver might report a
thermal update, but the temperature reported to the core won't
necessarily match what interrupt was meant for.
I have a patch that adds a thermal_zone_device_update_temp() API, so
drivers can report the temperature along with the interrupt
notification. (Such a patch also helps so that the driver can choose to
round down on cold events and up on hot events, resolving your rounding
issue too.)
Brian
--